 Post subject: Arc Flash analysis for Arc Resistance Switchgear.
PostPosted: Fri Jul 28, 2023 4:16 am 

Joined: Wed Apr 06, 2011 2:20 pm
Posts: 22
Do we need to do Arc Flash analysis for Arc resistance switchgear since you are still exposed to bus when you open the cubicle of the switchgear.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash analysis for Arc Resistance Switchgear.
PostPosted: Mon Jul 31, 2023 1:17 pm 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 566
Location: Wisconsin
abk453 wrote:
Do we need to do Arc Flash analysis for Arc resistance switchgear since you are still exposed to bus when you open the cubicle of the switchgear.


I don't know of any arc resistant gear that allows access to the power compartments while energized.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash analysis for Arc Resistance Switchgear.
PostPosted: Mon Jul 31, 2023 4:15 pm 
Sparks Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 286
Location: Indiana
JBD wrote:
abk453 wrote:
Do we need to do Arc Flash analysis for Arc resistance switchgear since you are still exposed to bus when you open the cubicle of the switchgear.


I don't know of any arc resistant gear that allows access to the power compartments while energized.


Square D PremSet fully insulated bus, 15kv.

_________________
SKM jockey for hire


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash analysis for Arc Resistance Switchgear.
PostPosted: Wed Aug 02, 2023 1:13 pm 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 566
Location: Wisconsin
bbaumer wrote:
JBD wrote:
abk453 wrote:
Do we need to do Arc Flash analysis for Arc resistance switchgear since you are still exposed to bus when you open the cubicle of the switchgear.


I don't know of any arc resistant gear that allows access to the power compartments while energized.


Square D PremSet fully insulated bus, 15kv.


I remember, tThe ones I worked on had interlocks with the power panel access doors.
If the doors are open, say when they are bypassed during maintenance, the gear probably is no longer rated as arc resistant, which usually needs sealed enclosures.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash analysis for Arc Resistance Switchgear.
PostPosted: Fri Aug 18, 2023 8:54 am 

Joined: Fri Aug 18, 2023 8:45 am
Posts: 2
bbaumer wrote:
JBD wrote:
abk453 wrote:
Do we need to do Arc Flash analysis for Arc resistance switchgear since you are still exposed to bus when you open the cubicle of the switchgear.


I don't know of any arc resistant gear that allows access to the power compartments while energized.


Square D PremSet fully insulated bus, 15kv.


Hello. My understanding the situation is not permitted with compartment door interlock.
It's better to clarify with original manufacturer and request evidence of the test condition in arc test.
I think the defined arc test in medium voltage busbar compartment is with the condition that compartment door closed.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash analysis for Arc Resistance Switchgear.
PostPosted: Sat Nov 11, 2023 9:26 am 

Joined: Fri Aug 22, 2014 2:31 pm
Posts: 10
Here is my understanding of arc resistant gear:
1. There is a maximum fault current and duration for which the gear is rated.
2. When racking in/out breakers, there is a chance of an arc flash event, but this presents no danger to the operator as long as the current level and duration is less than the SWGR rating.
3. After a breaker is racked out, the shutters are covering energized bus.
4. Because of #3, opening a door and removing a breaker doesn't result in an arc flash hazard. Furthermore, troubleshooting the circuitry in the cubicle with the shutters in place doesn't involve an arc flash hazard.

Obviously, if another person is racking out another breaker on the lineup while someone is troubleshooting circuitry, then there would be arc flash hazard to the person troubleshooting circuitry.

In my opinion, determining an arc flash hazard is balancing act that must take into account the qualifications of the people involved.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883