Author |
Message |
Beca_Zion
|
Post subject: how can I detect the arc flash level at the VSD point in SKM Posted: Sun Jan 28, 2024 3:30 pm |
|
Joined: Wed Jan 24, 2024 3:26 pm Posts: 3
|
Hi,
Why SKM doesn't to detect the arc flash level at the VSD bus however it can detect the CB's bus, the bus before and the bus after VSD? is there is a way to able to detect the fault level at the VSD bus?
Thanks
|
|
Top |
|
 |
bbaumer
|
Post subject: Re: how can I detect the arc flash level at the VSD point in Posted: Sun Jan 28, 2024 3:42 pm |
|
Sparks Level |
 |
Joined: Fri Jul 08, 2016 10:01 am Posts: 374 Location: Indiana
|
Not sure I'm interpreting your question correctly but if so you can add a bus to represent the line side of the drive then connect the drive to that bus. You'll have to give the bus some enclosure properties if you don't want to use panel as the default.
_________________ SKM jockey for hire PE in 16 states
|
|
Top |
|
 |
mpparent
|
Post subject: Re: how can I detect the arc flash level at the VSD point in Posted: Tue Jan 30, 2024 1:52 pm |
|
Joined: Thu Apr 18, 2019 11:42 am Posts: 133
|
Don't recall, but is there a node bus on the ins/outs of a VFD model in SKM? If so, just expand the node.
Mike
|
|
Top |
|
 |
Beca_Zion
|
Post subject: Re: how can I detect the arc flash level at the VSD point in Posted: Tue Feb 20, 2024 4:44 am |
|
Joined: Wed Jan 24, 2024 3:26 pm Posts: 3
|
Yes, I had to add a bus before the VSD and It worked! I really appreciate the help.
Cheers
|
|