It is currently Tue Mar 25, 2025 2:09 am



Post new topic Reply to topic
Author Message
 Post subject: how can I detect the arc flash level at the VSD point in SKM
PostPosted: Sun Jan 28, 2024 3:30 pm 

Joined: Wed Jan 24, 2024 3:26 pm
Posts: 3
Hi,

Why SKM doesn't to detect the arc flash level at the VSD bus however it can detect the CB's bus, the bus before and the bus after VSD? is there is a way to able to detect the fault level at the VSD bus?

Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: how can I detect the arc flash level at the VSD point in
PostPosted: Sun Jan 28, 2024 3:42 pm 
Sparks Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 374
Location: Indiana
Not sure I'm interpreting your question correctly but if so you can add a bus to represent the line side of the drive then connect the drive to that bus. You'll have to give the bus some enclosure properties if you don't want to use panel as the default.

_________________
SKM jockey for hire
PE in 16 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: how can I detect the arc flash level at the VSD point in
PostPosted: Tue Jan 30, 2024 1:52 pm 
Sparks Level

Joined: Thu Apr 18, 2019 11:42 am
Posts: 133
Don't recall, but is there a node bus on the ins/outs of a VFD model in SKM? If so, just expand the node.

Mike


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: how can I detect the arc flash level at the VSD point in
PostPosted: Tue Feb 20, 2024 4:44 am 

Joined: Wed Jan 24, 2024 3:26 pm
Posts: 3
Yes, I had to add a bus before the VSD and It worked!
I really appreciate the help.

Cheers


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883