Several Circuit Breakers failed on Short Circuit Study,at what point if any is this an option to replace? :confused:
PostPosted: Fri Dec 25, 2009 6:13 pm
Reducing the fault current sometimes is a better option, but if this is all you have failed you can easily upgrade these to higher interupting breakers, we provide these upgrades everyday and give exchanges for your old ones.
PostPosted: Fri Dec 25, 2009 7:13 pm
Are the failed breakers rated SC symmetrical or asymmetrical fault current?