OK, here are some other answers
Arc Flash Don wrote:
Here are six questions about Arc Flash Compliance and Analysis. Please comment.
1. Is PPE required to pull a simple disconnect switch to de-energize an enclosure with the cover closed?
Depends on the amp-cycles and class of switch, yes you need PPE, what level depends on the switch type and system charteristics. Unless it is arc rated switchgear, then no PPE required.
2. After an enclosure is de-energized by pulling the disconnect, is PPE required to test and verify the absence of voltage?
Yes, and the meter needs to be verified on a know live source, and possibly protective grounds installed, then you can relax PPE.
3. Pulling the disconnect switch on an enclosure de-energizes all the downstream circuits inside the enclosure. The incoming power to the switch contacts are still live. Therefore, Is the enclosure considered to be still energized or is it de-energized? How do other companies handle this problem?
Haze answered this pretty well, this is being discussed by 70E task force right now, newer equipment is being made with "arc safe" barriers for the live parts, but jury is out on how to handle older equipment. You can use arc flash suppression blankets for this.
4. Are gloves required for Hazard Categories 0 and 1? NFPA 70E Table 130.7(C)(10) is not clear regarding use of gloves for Hazard Categories 0 and 1. Are gloves required for shock hazard, even if they are not required for Arc Flash Hazard? If so, what type of gloves are acceptable for shock hazards?
Table 130.7(C)(10) has nothing to do with shock hazards, rubber gloves rated for the voltage levelk involved are always required when crossing the RAB.
5. Installing or replacing Bus Plugs on an energized Busway. I assume this is an example of live work requiring a work permit. Some people may disagree. Please provide clarification.
Not live work, treated just as racking in a circuit breaker, but as you know is more difficult and has higher risks involved, expect to see bus plugs added top the tables for 2009 revision (See ROP on NFPA website for details)
6. Do you know how other companies handle 480 Volt arc welders for their Arc Flash Study? We have a significant number which may affect our results.
Depends on the saftware you are using