What is the general consensus on the use of Tic Tracers when it comes to establishing/verifing an electricaly safe working condition? Personnally, I do not feel that they can be used in this process since there is no way to test a conductor phase to phase or phase to ground. Any thoughts would be greatly appreciated.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jun 10, 2010 4:04 pm 
Offline
Sparks Level

Joined: Wed Sep 23, 2009 9:29 pm
Posts: 83
Location: Western Canada
They do not meet the intent of contact testing. Troublesome part is that they are the defacto standard for testing at voltages over 750 volts. Contact testing at 600 volts (p-p) with a properly rated meter is what we do. We use a Salisbury 4356 tester for voltages above 600 volts.
No-one complains because the tester is a self check type...

Maybe somebody does something better out there?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jun 10, 2010 6:47 pm 
Offline
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
cbauer wrote:
What is the general consensus on the use of Tic Tracers when it comes to establishing/verifing an electricaly safe working condition? Personnally, I do not feel that they can be used in this process since there is no way to test a conductor phase to phase or phase to ground. Any thoughts would be greatly appreciated.


Yep, tricky one. My rule has been if I will touch it, do direct contact. If I don't plan on touching anything, proximity test is OK.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jun 11, 2010 9:37 am 
Offline

Joined: Sat Mar 06, 2010 6:07 am
Posts: 8
I too use the Salisbury tester for 600V>. I have trusted this on all jobs we de-energize both less than and greater than 600V.

Believe me, I test the bus and terminations many times over and over, goto an extension cord, goto a fluorescant light fixture and back again.

Caution on shielded and lead cables. I don't trust it then.

Then always suit up and use discharge stick and ground cables if our work requires contact or not.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jun 11, 2010 10:12 am 
Offline
Sparks Level

Joined: Mon Mar 29, 2010 11:52 am
Posts: 110
Location: Yankton SD/ Lead SD
I appreciate the responses. We do have a high voltage contact meter, but the crews generally perfer the use of 'proximatity' testers, unless they actually want to get a voltage measurement. I believe that in order to comply with the intent of 70E that the contact meter must be used.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883