 Post subject: Arc Flash Incident - Calculation Help
PostPosted: Wed Jul 07, 2010 8:31 am 

Joined: Wed Feb 17, 2010 1:08 pm
Posts: 4
Hello guys.

We had an incident where a 480V cable was run overhead for temporary power. A large vehicle was passing underneath the cable and the cable got caught on the vehicle. The insulation on the cable was damaged and caused arcing to the vehicle.

I have been asked to analyze the arc flash potential from this incident and I am a little confused on how to go about this for this situation.

The cable is fed from a delta-delta connected transformer so there should be no single-line-to-ground fault current. We have both SKM and ArcPro software programs. I was planning on using ArcPro for the analysis since it occured in open air but ArcPro is based on a single-phase model and since there is no SLG fault current I was not sure if using the three-phase fault current would give an accurate value. I also had questions as to the arc gap since it is a cable and not a bare wire installed overhead. Typically I would use a 2 inch arc gap for an overhead 480 V line.

Any help would be appreciated.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Jul 07, 2010 10:56 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 557
Location: Wisconsin
Is this part of a lawsuit?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Jul 07, 2010 11:19 am 

Joined: Wed Feb 17, 2010 1:08 pm
Posts: 4
JBD wrote:
Is this part of a lawsuit?


Nope. I believe our safety department would just like to know how serious this could have been.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Jul 07, 2010 3:30 pm 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 557
Location: Wisconsin
Unless all three phase conductors were damaged and the arcing was phase-phase-phase, doing a standard arc flash analysis may provide meaningless results. Normal SKM calculations, based on IEEE-1584, are not valid for single phase (either L-L or L-G) faults.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jul 08, 2010 6:39 am 

Joined: Wed Feb 17, 2010 1:08 pm
Posts: 4
JBD wrote:
Unless all three phase conductors were damaged and the arcing was phase-phase-phase, doing a standard arc flash analysis may provide meaningless results. Normal SKM calculations, based on IEEE-1584, are not valid for single phase (either L-L or L-G) faults.


Would ground faults even produce an arc flash due to the source being a delta-delta transformer?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jul 08, 2010 6:46 am 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
Have you checked to see if you already have a ground on one phase?


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883