After numerous go arounds with a utility reluctant to provide available fault current data, and given our reluctance to storm the place with pitchforks and tourches, we were able to extract the following information:
The facility in question is fed from a substation with 3- 40 MVA transformers, "477 conductor" and nominal voltages of 139kV/12.4kV.
I am assuming that "477 conductor" means 477MCM and the conductor is almost certainly aluminum. We measured the transmission distance to the substation at 4.5 miles.
Now, a quick back of the envelop calculation using a table impedance value for 500MCM AL (wich is what I have handy) and guessing about 8% impedance for the transformer and 1% for the source, I am comming up with about 3800A which seems a fairly reasonable start.
My question is, Does anyone know what a reasonable impedance range for a 40MVA transformer might be.
Any input would be appreciated.

Bob Ragsdale, PE


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Jul 28, 2010 8:26 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 631
Assuming the primary BIL is 550, ANSI C57.12.10 says 9.0% without load tapchanging and 9.5% with.

Note that with three transformers, there are three possible system configurations (source impedances) right there (neglecting all the other possible system changes the utility may make.)


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Aug 11, 2010 3:52 pm 
Sparks Level

Joined: Mon Dec 14, 2009 4:24 pm
Posts: 61
I believe you mean C57.12.10


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Aug 12, 2010 8:05 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 631
Fixed on edit. Thanks.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883