After doing a handfull of studies now, I am starting to see a trend with extremely high HRC levels for our Fire Pump Panels. While trying to mitigate these levels I am aware of the following limitations in the code:
695.5 Transformers
1. The transformer must be sized to at least 125 percent of the sum of the loads. (Fire Pump MTR plus Jockey Pump)
2. The transformer primary overcurrent device must be at least a specified minimum size.
3. The transformer secondary must not contain any overcurrent devices whatsoever.
With this in mind, I have no my wiggle room for recommendations to lower these findings.
Has anyone else seen this trend on Fire Pump Panels? Is there a way to mitigate the AF without comprimising the integrity of the Fire Pump system.


You do not have the required permissions to view the files attached to this post.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jul 27, 2010 7:41 pm 
Offline
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
(I'm from Canada, code requirements will certainly vary)

Could you install a 1:1 isolation transformer between your step-down transformer and the load? Such a transformer is sometimes used to lower the bolted fault current when equipment wasn't properly chosen (AIC rating) to begin with, so I guess it could be used also to reduce the arc fault current (I know: lower current may lead to longer opening time, so YMMV).


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883