What does the following CT ratio feeding an 87T Differential Relay mean? 600/100-5 Do I use the 600 or the 100 as the primary ratio? |
|
| Author: | richxtlc [ Thu Aug 19, 2010 9:21 am ] |
| Post subject: | |
hastheknack wrote: What does the following CT ratio feeding an 87T Differential Relay mean?
600/100-5 Do I use the 600 or the 100 as the primary ratio? How many leads are coming out of the secondary? It may be a multi-ratio CT. MR 600/5 conn 100/5. |
|
| Author: | jghrist [ Thu Aug 19, 2010 1:34 pm ] |
| Post subject: | |
richxtlc wrote: How many leads are coming out of the secondary? It may be a multi-ratio CT. MR 600/5 conn 100/5.
This is generally what the underlining means. |
|
| Author: | hastheknack [ Mon Aug 23, 2010 7:05 am ] |
| Post subject: | |
Thanks guys for the info. After some digging I found that it was a Multi-Ratio (MR) CT with the 100 lead selected. |
|