Coordination & Short Circuit Study
https://brainfiller.com/arcflashforum/viewtopic.php?f=2&t=1284
Page 1 of 1

Author:  aregular [ Thu Sep 09, 2010 8:57 am ]
Post subject:  Coordination & Short Circuit Study

Hi,

Sorry if this is not the right forum to bring up this question or if it has been dealt with before.

If a spec calls for just coordination study - do I also need to perform short circuit study and include the results of this analysis in the report.

Now I know that short circuit calculations need to be performed as part of the coordination study to determine to what extent protective devices selectively coordinate. But I am just not sure if the results (probably a table indicating if switchboards'/panels' SC rating pass/fail in comparison to the calculated fault levels at these locations) shall be included along with the findings of the coordination study

Thanks for the help

Author:  jghrist [ Fri Sep 10, 2010 10:51 am ]
Post subject: 

There is no standard as to what to include in a coordination study report. Normally, you would include the results of the short circuit study. What results and to what detail is a matter of judgement and agreement with whoever you are doing the report for.

Page 1 of 1 All times are UTC - 7 hours