How is an AC to DC rectifier with a capacitor bank considered? Looking at a 3MW power converter system with a rectifier feeding DC to multiple DC to AC converters. The rectifier can be treated as being an AC supplied cabinet and the calculation is straightforward. The DC supplied cabinet is the question. If we assume it can't get any more energy than the AC to DC cabinet can supply it is a straightforward answer - same hazard level. If we have to consider the stored energy on the capacitor bank, what calculation do we use? The DC discussions I've seen are centered on systems with a battery bank of some sort. The capacitor bank will give a very high pulse of current but the total energy is limited until the bank is discharged to the level that will be sustained by the input rectifier. The total joules available is much less than even a relatively small battery bank.

Any thoughts?

Thanks,


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Nov 11, 2010 5:27 am 
Offline
Arc Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 679
Location: Rutland, VT
this is going from memory from awhile but aren't rectifiers usually limited on the output of current due to the electronics? For instance, the spec sheet on the rectifier may say max fault current output of X amps and shutdown in Y secs at Z amps.
This would give some boundaries on available fault levels.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Nov 11, 2010 6:47 am 
Offline
Sparks Level
User avatar

Joined: Tue Oct 26, 2010 5:00 pm
Posts: 115
Location: Maple Valley, WA.
For many rectifier systems, the fault current is only about 3 to 5 times full load current.

_________________
Robert Fuhr, P.E.; P.Eng.
PowerStudies


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Nov 17, 2010 3:54 pm 
Offline

Joined: Fri Oct 15, 2010 3:39 pm
Posts: 3
Rectifier capacity

Usually a rectifier circuits fault current at these power levels is limited by the impedance of the AC circuit. The semiconductors may fail shorted long before the fault clears if not properly coordinated with circuit protection on the AC side. If not properly protected the semiconductor may then become the fuse and open up.

If this is the only concern for ARC FLASH calculations then there is no problem, we have it covered. However, there is the capacitor bank with stored energy that has a very fast current rise time and a very high potential peak current but is limited in the total energy available. If we were to add the available energy in the capacitor bank to the calculated available energy from the AC connection would that be a valid/safe/conservative number?


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883