when calculating arc flash levels, is it preferred to use the secondary (IDMT overcurrent) protection relay settings or ar the primary protection relay settings used for the arc interruption times?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Dec 04, 2010 2:16 pm 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 557
Location: Wisconsin
william090773 wrote:
when calculating arc flash levels, is it preferred to use the secondary (IDMT overcurrent) protection relay settings or ar the primary protection relay settings used for the arc interruption times?


It depends.

For an arcing fault that 'involves' the secondary protective device (i.e. in the same enclosure), you would have to use the primary settings. For a fault sufficiently removed from the secondary device (i.e. in a different enclosure) then the secondary settings should be usable.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Dec 05, 2010 10:26 am 
Sparks Level
User avatar

Joined: Tue Oct 26, 2010 5:00 pm
Posts: 201
Location: Maple Valley, WA.
william090773 wrote:
when calculating arc flash levels, is it preferred to use the secondary (IDMT overcurrent) protection relay settings or ar the primary protection relay settings used for the arc interruption times?


Using the primary settings will most likely result in higher arc flash energies. This because the primary device is set to protect the primary of the transformer. If a fault occurs at the secondary windings or downstream, then to the primary device, it looks like a big overload (due to the current transformation), and it will take a considerable amount of time (it often exceeds the 2 second point) to trip.

This is why the area between the transformer secondary and the line side of the main service breaker is the most hazardous place to work. For larger transformers, it can be HRC 4 or even Dangerous.

Differential protection can solve this issue by creating a differential zone between the line side of the transformer primary device and the load side of the main breaker. If a fault occurs in this zone, it is quickly removed. Reducing the trip time will lower the arc flash energy.

_________________
Robert Fuhr, P.E.; P.Eng.
PowerStudies


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883