ekstra   ara
 Post subject: Defining "Major Modification" or "Renovation" for Arc Flash Study
PostPosted: Mon Dec 06, 2010 12:16 pm 

Joined: Mon Dec 06, 2010 12:05 pm
Posts: 1
Per NFPA 70E - 130.3, The arc flash hazard analysis shall be updated when a major modification or renovation takes place.

Does anyone know what constitutes a "renovation"? I understand that if you add a panel, MCC or switchgear that the arc flash analysis should be revisited. Where would one draw the line on when a study needs to be redone and does anyone have something in writing that clearly defines where this line is drawn?

Thank you


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Dec 06, 2010 12:34 pm 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 557
Location: Wisconsin
It all depends.

Are the results of the study affected?

Adding a 50HP motor to an existing MCC could be considered major.
But, replacing service entrance equipment while reusing all of the existing conductors and protective device settings could be considered as non-major.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Dec 06, 2010 8:50 pm 
Sparks Level

Joined: Mon Mar 29, 2010 5:02 am
Posts: 136
If you are adding or deleting major pieces to the Distribution System, I think a good design pratice would be to revisit the effected areas and modify the study as needed.. JMO...


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Dec 07, 2010 8:16 am 
Sparks Level
User avatar

Joined: Tue Oct 26, 2010 5:00 pm
Posts: 201
Location: Maple Valley, WA.
I believe that anything that will change the fault current (i.e. additions of large motors. New larger utility transformer installed, etc.) or any changes in the protective devices (manufacture or type) or their settings will impact the AF energy and boundary calculations. Furthermore, any new equipment must have AF labels with the HRC and AF Boundary listed.

In some cities in the State of Washington, it is manditory to include AF lables (with the details) for any new equipment installed. Please see the article -

http://www.powerstudies.com/AreyourSpecsReadyforWACitiesElectricalCode.htm

_________________
Robert Fuhr, P.E.; P.Eng.
PowerStudies


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Dec 07, 2010 8:31 am 
Sparks Level

Joined: Mon Mar 29, 2010 11:52 am
Posts: 110
Location: Yankton SD/ Lead SD
I would agree with both glen1971, and Robertefuhr. Anytime that you modify a system to taht extent you need to re-evaluate how these changes effect the total system.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883