Hello: I have a question the use of primary transformer side fuses to control the secondary side IE before the main overcurrent protective device.
1. I have current limiting fuses on the primary side of my 2400V/480V transformer
2. My calculated short circuit on the secondary is the transformer is 15kA.
3. The primary would see 15kA * (480/2400) amperes.
4. I want use this the 'relfected' value in the primary tcc curve to when the fuse would clear and thus reduce the IE.

This is used in withstand curves so why not use in arc flash calculations?

Thanks for anyone's help here.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Feb 04, 2011 11:57 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Is the 15 kA the three phase arcing short circuit current? If it is then you can reflect it to the primary. Often the primary current in that situation is quite low. With "typical" oversized fuses or primary relay settings, the Ei becomes quite large - because of the long clearing time.

If it is a line-ground fault/arc flash that does not escalate into three phase, the primary current will only be 57.7% of its reflected value on delta wye transformers. Similar situation with delta-delta and line-line faults (same concept used when shifting the ANSI C57 thru fault curves for protection)

Hope it helps - let me know if you any other info.

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Feb 04, 2011 1:08 pm 

Joined: Mon Dec 08, 2008 7:52 pm
Posts: 8
Thanks for info

Your answer helped me a lot. Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Feb 04, 2011 2:40 pm 
Arc Level

Joined: Thu Jan 10, 2008 8:49 pm
Posts: 520
Location: New England
Just make sure you know that arcing fault current, and calculated fault current are two different things. So that you are both talking about the same terms, as my initial impression was that you were taking 'fault current' on the secondary and not arcing fault current.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Feb 05, 2011 9:45 am 

Joined: Mon Dec 08, 2008 7:52 pm
Posts: 8
arc flash current through transformer

got it. Thanks,


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883