Post subject: transformer secondary side arc flash Posted: Fri Feb 04, 2011 11:14 am |
|
Joined: Mon Dec 08, 2008 7:52 pm Posts: 8
|
Hello: I have a question the use of primary transformer side fuses to control the secondary side IE before the main overcurrent protective device.
1. I have current limiting fuses on the primary side of my 2400V/480V transformer
2. My calculated short circuit on the secondary is the transformer is 15kA.
3. The primary would see 15kA * (480/2400) amperes.
4. I want use this the 'relfected' value in the primary tcc curve to when the fuse would clear and thus reduce the IE.
This is used in withstand curves so why not use in arc flash calculations?
Thanks for anyone's help here.
|
|
Top |
|
 |
Jim Phillips (brainfiller)
|
Post subject: Posted: Fri Feb 04, 2011 11:57 am |
|
Plasma Level |
 |
Joined: Mon Sep 17, 2007 5:00 pm Posts: 1710 Location: Scottsdale, Arizona
|
Is the 15 kA the three phase arcing short circuit current? If it is then you can reflect it to the primary. Often the primary current in that situation is quite low. With "typical" oversized fuses or primary relay settings, the Ei becomes quite large - because of the long clearing time.
If it is a line-ground fault/arc flash that does not escalate into three phase, the primary current will only be 57.7% of its reflected value on delta wye transformers. Similar situation with delta-delta and line-line faults (same concept used when shifting the ANSI C57 thru fault curves for protection)
Hope it helps - let me know if you any other info.
_________________ Jim Phillips, P.E. Brainfiller.com
|
|
Top |
|
 |
beenthere
|
Post subject: Posted: Fri Feb 04, 2011 1:08 pm |
|
Joined: Mon Dec 08, 2008 7:52 pm Posts: 8
|
Thanks for info
Your answer helped me a lot. Thanks
|
|
Top |
|
 |
haze10
|
Post subject: Posted: Fri Feb 04, 2011 2:40 pm |
|
Joined: Thu Jan 10, 2008 8:49 pm Posts: 520 Location: New England
|
Just make sure you know that arcing fault current, and calculated fault current are two different things. So that you are both talking about the same terms, as my initial impression was that you were taking 'fault current' on the secondary and not arcing fault current.
|
|
Top |
|
 |
beenthere
|
Post subject: Posted: Sat Feb 05, 2011 9:45 am |
|
Joined: Mon Dec 08, 2008 7:52 pm Posts: 8
|
arc flash current through transformer
got it. Thanks,
|
|