haze10 wrote:
Just being in an MCC room does not necessitate arc flash clothing unless there is significant energy being switch, ie switchgear. MCC's and panelboards do not routinely fit this definition. So if all doors are closed and there are no exposed live parts, there is no HRC clothing required.
You could argue that using the station control system to operate the MCC is interacting with the MCC. Then you would need to be outside the arc hazard boundary to be without PPE.
Prudence would dictate locating the controls outside the boundary if an operator is at the PC monitor for long periods of time, regardless of whether the MCC is controlled at the monitor location. Operation of starters or breakers by others would require the operator to move away from the MCC.