TheArk wrote:
We would then pursue identification and labeling of circuits that potentially fall outside of that status, i.e.; extremely long circuit conductors or isolation transformer installations, etc.
Equipment on long circuit conductors may well have higher incident energy levels that at the MCC. If the fault current drops below a short time or instantaneous pickup value, the clearing time could increase significantly and may exceed the table assumptions.