 Post subject: Motor Contribution Too High
PostPosted: Wed Mar 30, 2011 1:20 pm 
Offline

Joined: Tue Mar 29, 2011 4:54 am
Posts: 3
I'm using SKM Power Tools in a study. The facility has 15 Motors over 50hp. The Isc 3P feed back to the main breaker is calculated at 69,390 A. This seems way to high when the main feed is only 38,157 A.
Is this normal?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Mar 30, 2011 1:47 pm 
Offline
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 409
Location: Spartanburg, South Carolina
Total HP? Voltage?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Mar 31, 2011 4:19 am 
Offline

Joined: Tue Mar 29, 2011 4:54 am
Posts: 3
1200 HP Total, 480V


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Mar 31, 2011 7:50 am 
Offline
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 409
Location: Spartanburg, South Carolina
A rough approximation of motor contribution would be to assume 6 times FLA and HP = kVA, so 1200 HP would have 6*1200/0.48/sqrt(3) = 8,660 A fault contribution. There is a problem with the 69,390 A value.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Mar 31, 2011 8:43 am 
Offline

Joined: Tue Feb 16, 2010 7:59 am
Posts: 21
Location: Minneapolis, MN
If you are using SKM, in your motor data pages check what you have in the LRA/FLA field (locked rotor to full load, the default is 5.88). Did you accidentally enter a HP value in one of these fields for a motor?

Bob Ragsdale P.E.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Apr 01, 2011 4:51 am 
Offline

Joined: Tue Mar 29, 2011 4:54 am
Posts: 3
Thank you both for your help. I entered the FLA in the LRA/FLA field for the motors. Once changed, it looks much better. Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Apr 01, 2011 6:29 am 
Offline

Joined: Tue Feb 16, 2010 7:59 am
Posts: 21
Location: Minneapolis, MN
Not that I've ever done that.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Apr 01, 2011 11:13 am 
Offline

Joined: Mon Jan 26, 2009 5:00 pm
Posts: 46
Location: Midwest
;)
Me either!


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 8 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883