It is currently Fri Oct 02, 2026 12:25 pm



Post new topic Reply to topic
Author Message
 Post subject: Label Low Voltage Transformers?
PostPosted: Tue May 03, 2011 7:50 am 

Joined: Thu Oct 08, 2009 12:16 pm
Posts: 13
Location: St. Paul, MN
I have a question. In our industry we work a lot with dry type transformers with a 480V primary and a 208 or 240V secondary. Typically these transformers are under 125kVA. When I run calcs, typically the secondary side has a higher hazard than the primary. So my questions are:

1) Do you typically apply a label to the transformer?

2) If yes to #1, does the label represent the primary or secondary side hazard, even though the secondary is 240V or less?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue May 03, 2011 8:20 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 616
Location: Wisconsin
Think about how a small transformer is built, the terminals are effectively: LV-HV-LV-HV-LV-HV-LV. It is almost impossible to have a L-L fault on the secondary that does not create a L-L fault on the primary.

However, when a customer requires a label on a transformer we will use the worst case AFIE and the highest voltage, irrespective of if it is on the primary or secondary.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue May 03, 2011 8:36 am 

Joined: Thu Oct 08, 2009 12:16 pm
Posts: 13
Location: St. Paul, MN
Thanks for the replay, so is it industry standard to place a lablel on the transformer?

Perhaps I have something set wrong with in my EasyPower, but typically the higher voltage has a lower AFIE, so when you say worst case and highest voltage are you refereing to two lables (typically the 480V side is Class 0 and the secondary side comes up as Class 1 or 2)


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue May 03, 2011 9:25 am 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
If it is 208 volt and under 125 kVA, then it falls under Exception No. 1 to 130.3 and analysis is not required for the secondary. If the primary is higher than 1.2 cal/cm² then it needs a label more than Cat 0.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue May 03, 2011 9:39 am 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 616
Location: Wisconsin
ronlow00 wrote:
Thanks for the replay, so is it industry standard to place a lablel on the transformer?

Perhaps I have something set wrong with in my EasyPower, but typically the higher voltage has a lower AFIE, so when you say worst case and highest voltage are you refereing to two lables (typically the 480V side is Class 0 and the secondary side comes up as Class 1 or 2)


Your program is probably providing correct results. It is extremely unlikely that a secondary fault will cause the primary devices to operate very fast, resulting in a very long clearing time.

We use a single custom label, listing the highest voltage (in most cases the primary) and the highest PPE category (in most cases on the secondary). In general, I am not a believer in multiple labels on a single device.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883