 Post subject: What happened to the D.8 tables in NFPA 70E 2012?
PostPosted: Wed Mar 14, 2012 10:55 am 
Sparks Level

Joined: Mon Dec 14, 2009 4:24 pm
Posts: 61
I'm looking for the tables in NFPA 70E 2012 that were in section D.8 under the title: "Estimated Incident Energy Exposures for Live Line Work on Overhead Open Air Systems 1kV to 800kV".

They don't appear to be in 70E 2012 yet the corresponding tables are still in NESC 2012... What am I missing?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Mar 29, 2012 8:11 am 
Sparks Level
User avatar

Joined: Wed Jun 10, 2009 5:00 pm
Posts: 267
Location: Toronto
good question. would be nice to hear from someone involved in NFPA 70E 2012 development what's happening to section D.8 and the reason why the section does not appear in the new standard edition?

_________________
Michael Furtak, C.E.T.
http://arcadvisor.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Mar 30, 2012 3:21 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2173
Location: North Carolina
My guess would be that since there is no direct coordination between the 70E Committee and the NESC Committee (unlike say CSA Z462), they probably deleted them not knowing what the NESC was going to do. This is similar to where the "low voltage exception" which used to quote IEEE 1584 (less than 125 kVA, 240 volts, one transformer) has been removed from 70E, at least temporarily.

The tables did change drastically, for the <15 kV section...for the most part they now refer to NFPA 70E or EPRI data. Above that value, they still use values calculated from ArcPro, just as in the 2012 edition.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Mar 30, 2012 8:29 am 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
PaulEngr wrote:
The tables did change drastically, for the <15 kV section...for the most part they now refer to NFPA 70E or EPRI data. Above that value, they still use values calculated from ArcPro, just as in the 2012 edition.

I think you mean <1 kV.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Apr 02, 2012 11:09 am 
Sparks Level

Joined: Mon Dec 14, 2009 4:24 pm
Posts: 61
Thanks


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883