It is currently Sun Sep 27, 2026 6:56 am
 Post subject: Burndown article
PostPosted: Thu Jun 07, 2012 6:46 am
I recall seeing an IEEE published article from way back, probably 1960's or 1970's vintage, discussing the subject of burndown and high resistance ground failures which operate undetected.
Does anyone know where this is at, article title, or other pointers?
PostPosted: Thu Jun 07, 2012 8:09 am
[SIZE=3]Predicting Damage from 277-V Single Phase to Ground Arcing Faults[/size]
[url='http://www.arcflashforum.com/researcher/29936621_Harris_I_Stanback']Harris I. Stanback[/url]
Square D Company, Lexington, KY 40505
Not sure if this is the one you were looking for but it was pretty good and from that time frame. I was at Square D when Harry was the Chief Engineer. He conducted much of the research in this area.
Jim Phillips, P.E.
Brainfiller.com
PostPosted: Thu Jun 07, 2012 12:30 pm
You can buy it at
http://ieeexplore.ieee.org/xpl/articleDetails.jsp?arnumber=4503412
See Eaton white paper
TP08700001E
[SIZE=4][color=#ffffff][font=Univers-Bold][SIZE=4][color=#ffffff][font=Univers-Bold][/font][/color][/size][/font][/color][/size]
PostPosted: Mon Jun 11, 2012 2:52 pm
Beeman's handbook om power systems covered this but it is probably out of print.