PaulEngr wrote:
There are LOTS of better ways. Almost all current efforts are directed towards decreasing trip times and/or increasing distances to the point where incident energy is as low as practical. Structural changes such as splitting up transformers can make a big difference but requires someone to plan this into the design.
Excellent comment - I just did a job with two 800 amp service switchboards located in a building. They were fed by a single 1000 kva transformer owned by the utility. The service disconects were the main 800 amp breakers in each switchboard. In this scheme both switchboards were over 40 ca/sq cm. We changed the design to two outdoor 800 amp customer owned fusible switches. The switchboards in the building were now a HRC #1. We also removed the two 800 amp breakers from the switchboards inside the building, therefore, the cost was the same or less and the arc flash was controllable.