Quote:
Hey guys just registered here but have been reading through the forums. I have a question regarding working distance and what is the reference used? For example we have a 15kV breaker that needs to be racked in. Is the distance measure from the stabs at the back of the breaker or the closest point on the breaker itself that will be energzied such as the top end of the vacuum bottles?
The 1584 Committee used the distance between the chest area and the bus bars at the back of the enclosure for the table. For 15 kV I believe (don't have it in front of me) this is 36". Generally everyone just uses the tables and does not actually physically measure it except if they have an unusual circumstance such as if you are operating a pole mounted interruptor with a hot stick in which case the 36" value is vastly lower than the real world case.
Quote:
Also on a side note I have read several posts on doors closed/open. Does anyone here allow for a downgrade in PPE while racking operations due to the door being closed? If there is already a thread on the subject could you give a link I tried searching and did not come up with anything here.
Rack mounted breakers have the highest rate of failure according to IEEE 493 data among other sources. This is pretty obvious simply because there are vastly more moving parts in rack mount equipment than in bolted ones. CIGRE has performed a study and found that arcing faults in this type of breaker happen 80% of the time at the stabs. IEEE 1584 (the most popular source for incident energy calculations) and 70E among others clearly indicate that although doors provide SOME protection to thermal energy, the reduction is variable and varies by design, size, and manufacturer to the point where they simply err on the conservative side and ignore it. Generally doors also turn into projectiles in many cases. Finally with regards to reducing PPE, are you nuts? This is absolutely the most patently stupid idea anywhere in 70E. The incident energy does not decrease due to the task...the likelihood of an arc flash (and thus the RISK) decreases. So either you are wearing adequate PPE as calculated or you aren't. The tables should say X or ZERO, not X, X-1, X-2, etc.
Quote:
One other item- what is the highest calculation that you have seen? I just started a new job and a facility that I have not worked in before. They have some stickers on some 480 gear that over 5000 cal. An no that is not a typo.
This is 99% likely to be the engineers screw up. Many engineers have made two serious mistakes in the past. First, they used an equation that is very simple developed early on that treats voltage and current the same. It generates values that are way above anything ever actually measured. This leads to an answer but it is usually wildly incorrect.
Second, they use their old short circuit calculations and simply ignore short circuit decreases due to cabling. For short circuit calculation purposes this leads to safe (conservative) values. However for incident energy it doesn't. The short circuit is used to determine how fast the breaker opens. Lower currents generally lead to much longer breaker or fuse opening times, and higher overall incident energy.
Using 70E, anything over 40 cal/cm^2 is stated as the condition where due to the concussive force of an arc blast, you won't survive it anyway. There is ongoing research on this but for right now the assumption used is that over 40 cal/cm^2, no amount of PPE is going to protect you anyways. So it really doesn't matter if the incident energy is 41 cal/cm^2 or 5000 cal/cm^2 because it is treated identically for PPE purposes.
For the record a few areas in the plant I work at have incident energy values into the hundreds. The working distances are listed so large that basically, it encompasses the entire plant site. This is obviously not physically possible but points out the fact that when it comes to this particular equipment, working live is simply not an option.