I am doing an arc flash assessment and have came across a strange observation. Wanted to get some confirmation from others experience....

I have a LV system (0.415kV) fed by transformer (3.3/0.415 kV) protected by a 250A HRC fuse (GE K81 PEX) for shortcircuit on HV feeder. For a fault level on 0.415V LV side (~19kA 100ms symmetrical rms), the fault current seen by fuse on HV is around 2kA. As per the pre-arcing time vs. prospective current graph of fuse, it will melt in 4s. This gives a hazard category of X

My take on the observation is: Fault current on LV is much less than the switchgear rating (63kA), which when reflected on primary would be even less ..... hence fuse take more time to trip this giving high hazard category.

Want to confirm I am not doing anything wrong. And such observations with LV are usual???


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Jan 10, 2009 6:57 am 

Joined: Wed Nov 26, 2008 7:55 am
Posts: 44
Location: Connecticut
Energy & Time

You have just understood the relationship to the release of energy, and the time it takes to clear it.

Higher categories can be achieved at lower current levels when the time it takes to clear is excessive. Just like the sun, you can get a second degree burn if you are exposed too long.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Jan 10, 2009 7:07 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
varun.singhal wrote:
My take on the observation is: Fault current on LV is much less than the switchgear rating (63kA), which when reflected on primary would be even less ..... hence fuse take more time to trip this giving high hazard category.



Yes this is a typical problem for industrial plants, can be mitigated but not easy to do and expensive.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Jan 21, 2009 12:32 pm 
Sparks Level
User avatar

Joined: Mon Nov 10, 2008 1:08 pm
Posts: 60
Location: Cincinnat, OH
There is always the 2 second rule in the IEEE 1584. If you use this as a cut off time it may offer lower IE.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883