 Post subject: Arc Flash for SWBD c/w Main BKR & Feder BKR's
PostPosted: Wed Jan 14, 2009 8:22 am 

Joined: Thu Dec 11, 2008 9:45 am
Posts: 3
In regards to calculating energy and attaching arc flash labels to switchboards / panels (which has main breaker and many feeder breakers), I appreciate if anyone who's familiar with NFPA, IEEE and safety practices to clarify the following:
1-Where do we consider calculating the energy on the switchboard / panel (on the line side of the main breaker, or the load side of the main breaker)?
2-Do we require attaching labels on each breaker of the switchboard / panel ? If that’s requested by the client, in this case, do we consider calculating the energy after the breaker (on the load side) or before the breaker (on the line side) of each breaker ( Main or Feeder)?
I appreciate your opinions, Thank you !


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Jan 14, 2009 10:07 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Shereen wrote:
In regards to calculating energy and attaching arc flash labels to switchboards / panels (which has main breaker and many feeder breakers), I appreciate if anyone who's familiar with NFPA, IEEE and safety practices to clarify the following:


It sounds to me from your post that your company has been hired to do this analysis, I would hope that you are familar with NFPA 70E and IEEE.

Shereen wrote:
1-Where do we consider calculating the energy on the switchboard / panel (on the line side of the main breaker, or the load side of the main breaker)?


Both

Shereen wrote:

2-Do we require attaching labels on each breaker of the switchboard / panel ? If that’s requested by the client, in this case, do we consider calculating the energy after the breaker (on the load side) or before the breaker (on the line side) of each breaker ( Main or Feeder)?



You calulate the Ei for the equipment, if you are talking about a breaker then you need to consider what is feeding it for your analysis.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883