PaulEngr wrote:
I've been doing a "data mining" exercise. I will post the results. The goal is to dig through OSHA accident investigation summary data to look for typical and/or likely tasks and activities that induce an arc flash. One potential issue with this data is that it is not comprehensive...it cannot be used for statistics such as average number of arc flash related fatalities per year. However one of the statistics really stands out so far: so far I have gone back to 2008 and have 68 serious injuries (requiring hospitalization), 14 minor injuries, and 4 fatalities.
There have been several similar analyses conducted that I'm aware of - I think one was presented at the Electrical Safety Workshop a few years ago, and one was presented at an IEEE 1584 working group meeting several years ago. Have you seen any of these? If not I can dig them up and send them to you, perhaps they have the data you are collecting and could simply be updated.
PaulEngr wrote:
It would seem that 70E is pretty darned vague on specifics on meters, and maybe contributes to a lack of understanding of just how to actually test for absence of voltage, and what "absent" means (0 volts? <50 volts? <250 volts?)
NFPA 70E-2012 section 110.4 has an informational note about meter ratings. Sections 110.4 and 130.2(A) seem to imply that we need to be more excited about voltages >50 volts than those voltages lower than 50 volts. Granted this is vague, but it has convinced my company to disallow the common low voltage capacitive voltage detectors because most of the ones rated to detect up to 600V are NOT rated to detect below 90V.....