wilhendrix wrote:
Here's an example: suppose you have an MCC with several underrated circuit breakers installed in it. The maximum calculated fault current is 36,000 amps, but the circuit breakers are only rated at 35,000 AIC. Suppose one of these breakers had a 36,000 amp fault and suppose it failed and ruptured. Does the arc flash energy change? If so, does it go up or does it go down?
You now have two separate locations where arcs are occurring, so you have increased the hazard. The worker at the downstream fault location has increased exposure due to the longer exposure time waiting for the backup device to clear. Some of the energy is diverted to the overdutied arcing MCC breaker, but I know of no good way to estimate it. And then you have the worker walking by the overdutied MCC breaker. Since he was not contemplating any interaction, he is not wearing PPE will be exposed accordingly.