 Post subject: Minimum Approach Distances - Which ones?
PostPosted: Fri Feb 06, 2009 8:46 am 
Offline

Joined: Fri Feb 06, 2009 7:49 am
Posts: 1
Location: Lower Willamette Valley in Oregon
While minimum approach distances are unrelated to arc flash boundaries, they come into play for utility distribution voltages: If the arc flash boundary is less than the MAD, then it becomes a moot topic because the line worker will be futher away than the boundary. My question is this: Which MAD should utilities use? :confused: The numbers listed in OSHA 1910.269(I)(10), Table R-6 are different from those listed in the NESC, Tables 441-1 and 441-2, especially in the 15kV to 25kV range. Also, the separation of single phase and three phase distances in Tables 441-1 and 441-2 seems non-sensical. :eek:


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Feb 06, 2009 12:36 pm 
Offline
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 438
Note that the MAD is measured from the conductor, while the arc flash boundary is measured from the arc. Looks like NESC is more restrictive. If both apply, use the most restrictive. NESC usually leads OSHA. I expect the next OSHA revision will match NESC. There is an NESC Arc flash forum here.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883