| Author: | Eugineer [ Fri Feb 06, 2009 8:46 am ] |
| Post subject: | Minimum Approach Distances - Which ones? |
While minimum approach distances are unrelated to arc flash boundaries, they come into play for utility distribution voltages: If the arc flash boundary is less than the MAD, then it becomes a moot topic because the line worker will be futher away than the boundary. My question is this: Which MAD should utilities use? |
|
| Author: | stevenal [ Fri Feb 06, 2009 12:36 pm ] |
| Post subject: | |
Note that the MAD is measured from the conductor, while the arc flash boundary is measured from the arc. Looks like NESC is more restrictive. If both apply, use the most restrictive. NESC usually leads OSHA. I expect the next OSHA revision will match NESC. There is an NESC Arc flash forum here. |
|