Post subject: Question on a size of Arc Flash Posted: Thu Feb 19, 2009 7:52 am |
|
Joined: Thu Feb 19, 2009 7:45 am Posts: 4
|
Does anyone know what the results would be from a simple small distribution disconnect if it were short circuited and it had an arc flash. How large and destructive of an arc flash could this small of a device actually create?
|
|
Top |
|
 |
Zog
|
Post subject: Posted: Thu Feb 19, 2009 8:03 am |
|
Joined: Mon Jun 02, 2008 11:58 am Posts: 1103 Location: Charlotte, NC
|
Willis wrote: Does anyone know what the results would be from a simple small distribution disconnect if it were short circuited and it had an arc flash. How large and destructive of an arc flash could this small of a device actually create?
Depends on the available fault current and the clearing time of the protective device. Could potentially be a devesating arc flash that can destroy the equipment and injure persons anywhere in the room, or could be very minor and not dangerous, all depends on the factors involved.
|
|
Top |
|
 |
Noah
|
Post subject: Posted: Thu Feb 19, 2009 8:45 am |
|
Joined: Mon Apr 14, 2008 7:10 am Posts: 142
|
For small disconnect switch, sometime it is hard to find space on the switch to put a lable on. How do you guys deal with those devices? What if you have a row switches on the wall for pump/motor control?
|
|
Top |
|
 |
Willis
|
Post subject: Posted: Thu Feb 19, 2009 8:52 am |
|
Joined: Thu Feb 19, 2009 7:45 am Posts: 4
|
Clearing time
What do you mean "clearing time"?
|
|
Top |
|
 |
Zog
|
Post subject: Posted: Thu Feb 19, 2009 9:56 am |
|
Joined: Mon Jun 02, 2008 11:58 am Posts: 1103 Location: Charlotte, NC
|
Willis wrote: What do you mean "clearing time"?
How long it takes the fuse or breaker to clear the fault at different fault current levels.
|
|
Top |
|
 |
Willis
|
Post subject: Posted: Thu Feb 19, 2009 10:45 am |
|
Joined: Thu Feb 19, 2009 7:45 am Posts: 4
|
Thanks!
I appreciate the information Zog.
|
|
Top |
|
 |
Zog
|
Post subject: Posted: Thu Feb 19, 2009 12:02 pm |
|
Joined: Mon Jun 02, 2008 11:58 am Posts: 1103 Location: Charlotte, NC
|
|
Top |
|
 |
WDeanN
|
Post subject: Posted: Thu Feb 19, 2009 2:36 pm |
|
Joined: Thu Jul 19, 2007 7:54 am Posts: 201 Location: St. Louis, MO
|
How small is a small disconnect? If its fed by < 30A molded case breaker, it is likely to be < 4 cal/cm.
If it's fed by a 600A drawout breaker at a unit substation, it could be > 40 cal.
We actually have a case like this, where the breaker is used to feed several things, including a 70A 480V welding receptacle that is now >40 cal because they chose to feed it directly from the UnitSub.
Noah, if there is a wire trough above the disconnect rack, I would consider putting the label there, although I have also covered the factory markings at times (I do my best not to, though.)
|
|
Top |
|
 |
Willis
|
Post subject: Posted: Thu Feb 19, 2009 2:54 pm |
|
Joined: Thu Feb 19, 2009 7:45 am Posts: 4
|
How small is a small disconnect? If its fed by < 30A molded case breaker, it is likely to be < 4 cal/cm.
If it's fed by a 600A drawout breaker at a unit substation, it could be > 40 cal.
We actually have a case like this, where the breaker is used to feed several things, including a 70A 480V welding receptacle that is now >40 cal because they chose to feed it directly from the UnitSub.
What is the cal/cm range that an arc flash becomes deadly or cause serious injury?
|
|
Top |
|
 |
Zog
|
Post subject: Posted: Thu Feb 19, 2009 6:46 pm |
|
Joined: Mon Jun 02, 2008 11:58 am Posts: 1103 Location: Charlotte, NC
|
Willis wrote: What is the cal/cm range that an arc flash becomes deadly or cause serious injury?
1.2 cal/cm2 will cause second degree burns in 1/10th of a second. Put you in a burn unit, life changing event.
|
|
Top |
|
 |
|