 Post subject: Question on a size of Arc Flash
PostPosted: Thu Feb 19, 2009 7:52 am 

Joined: Thu Feb 19, 2009 7:45 am
Posts: 4
Does anyone know what the results would be from a simple small distribution disconnect if it were short circuited and it had an arc flash. How large and destructive of an arc flash could this small of a device actually create?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Feb 19, 2009 8:03 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Willis wrote:
Does anyone know what the results would be from a simple small distribution disconnect if it were short circuited and it had an arc flash. How large and destructive of an arc flash could this small of a device actually create?


Depends on the available fault current and the clearing time of the protective device. Could potentially be a devesating arc flash that can destroy the equipment and injure persons anywhere in the room, or could be very minor and not dangerous, all depends on the factors involved.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Feb 19, 2009 8:45 am 
Sparks Level

Joined: Mon Apr 14, 2008 7:10 am
Posts: 142
For small disconnect switch, sometime it is hard to find space on the switch to put a lable on. How do you guys deal with those devices? What if you have a row switches on the wall for pump/motor control?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Feb 19, 2009 8:52 am 

Joined: Thu Feb 19, 2009 7:45 am
Posts: 4
Clearing time

What do you mean "clearing time"?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Feb 19, 2009 9:56 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Willis wrote:
What do you mean "clearing time"?


How long it takes the fuse or breaker to clear the fault at different fault current levels.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Feb 19, 2009 10:45 am 

Joined: Thu Feb 19, 2009 7:45 am
Posts: 4
Thanks!

I appreciate the information Zog.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Feb 19, 2009 12:02 pm 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Welcome to the forum.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Feb 19, 2009 2:36 pm 
Sparks Level

Joined: Thu Jul 19, 2007 7:54 am
Posts: 201
Location: St. Louis, MO
How small is a small disconnect? If its fed by < 30A molded case breaker, it is likely to be < 4 cal/cm.
If it's fed by a 600A drawout breaker at a unit substation, it could be > 40 cal.
We actually have a case like this, where the breaker is used to feed several things, including a 70A 480V welding receptacle that is now >40 cal because they chose to feed it directly from the UnitSub.

Noah, if there is a wire trough above the disconnect rack, I would consider putting the label there, although I have also covered the factory markings at times (I do my best not to, though.)


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Feb 19, 2009 2:54 pm 

Joined: Thu Feb 19, 2009 7:45 am
Posts: 4
How small is a small disconnect? If its fed by < 30A molded case breaker, it is likely to be < 4 cal/cm.
If it's fed by a 600A drawout breaker at a unit substation, it could be > 40 cal.
We actually have a case like this, where the breaker is used to feed several things, including a 70A 480V welding receptacle that is now >40 cal because they chose to feed it directly from the UnitSub.


What is the cal/cm range that an arc flash becomes deadly or cause serious injury?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Feb 19, 2009 6:46 pm 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Willis wrote:
What is the cal/cm range that an arc flash becomes deadly or cause serious injury?


1.2 cal/cm2 will cause second degree burns in 1/10th of a second. Put you in a burn unit, life changing event.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 10 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883