 Post subject: 3P Fault current Vs SLG
PostPosted: Sat Feb 21, 2009 5:28 pm 

Joined: Thu Jan 29, 2009 2:06 am
Posts: 29
So I was looking over a study done by another firm and I noticed something that seemed odd. The single line to ground (SLG) fault current was almost as much as the 3 Phase fault current.

To me this does not make sense. For the sake of discussion let's say the available 3 Phase fault current was 53,000 they show a SLG of 50,000. Is there any thing that could possible cause this? The system is 480 and the utility feeds are 25kV into three 2500kVA TX to 480 with three utility input feeds at 4000A to the facility on three different busses.

thoughts?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Feb 21, 2009 5:39 pm 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
Abaolutely makes sense. If the supply transformer is delta-wye, the line to ground fault duty would be higher than the three phase at the secondary. This occurs because the only zero sequence impedance you have at the secondary of the transformer is the transformer Z. None of the zero sequence from the primary transfers from the delta connection.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Feb 21, 2009 5:57 pm 

Joined: Thu Jan 29, 2009 2:06 am
Posts: 29
I thought three phase bolted fault would be the worse case scenario?

And would therefore be able to supply a higher available fault current. Which it does, I suppose I just assumed there to be a greater difference.

I mean isn't the 3 Phase fault based on LLLG or is it just LLL

I think I confused myself...lol


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Feb 21, 2009 6:12 pm 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
Well, it is actually true that a delta-wye without a resistance grounded secondary will have a higher L to G than 3Ph. fault current. It will generally be higher downstream of the transformer until the negative sequence Z builds to the point that it equals the positive sequence.

If it is a wye-wye connection then this will not be the case.

IE doesn't necessarily follow that trend though if you are expecting a three phase fault instead of a single phase fault.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Feb 21, 2009 6:48 pm 

Joined: Thu Jan 29, 2009 2:06 am
Posts: 29
Hence symmetrical fault. I just figured that more "power" would be involved in a LLL than a SLG fault. I guess I was confusing IE with available fault current.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Feb 22, 2009 1:11 pm 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
SirSpark wrote:
Hence symmetrical fault. I just figured that more "power" would be involved in a LLL than a SLG fault. I guess I was confusing IE with available fault current.


There probably will be more energy involved in a LLL than SLG arcing fault even if the SLG fault current is higher. There are at least two arcs involved in a LLL fault and only one in a SLG fault.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Feb 22, 2009 3:04 pm 

Joined: Thu Jan 29, 2009 2:06 am
Posts: 29
Yeah it all makes perfect sense now I dont know what I was thinking...

I mean It is not Ia+Ib+Ic so why would fault current be any different....

So then if we are talking delta-wye and similar conditions as previously stated one should suspect something is wrong if the SLG was significantly lower than the 3P....


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Feb 22, 2009 5:06 pm 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
You should suspect something is wrong with a delta - solidly grounded wye if the L to G is not the highest available.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Feb 23, 2009 4:17 pm 

Joined: Thu Jan 29, 2009 2:06 am
Posts: 29
acobb wrote:
You should suspect something is wrong with a delta - solidly grounded wye if the L to G is not the highest available.


Sure enough I had my neutral impedance values incorrect on the transformers...


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Feb 23, 2009 6:12 pm 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
Good to get it figured out now instead of later!!! Glad it helped.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Feb 24, 2009 4:46 pm 

Joined: Thu Jan 29, 2009 2:06 am
Posts: 29
acobb wrote:
Good to get it figured out now instead of later!!! Glad it helped.


Thanks for your help...

Yeah I don't know what I was thinking, I was probably thinking to many things at once, the more I look at it the more it totally makes sense.

At least I knew enough that something was odd in my calculations to further research it....


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 11 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883