When analyzing a system, is there a regulation that states I must maintain selective coordination, when it has been violated?
|
|
Top |
|
 |
haze10
|
Post subject: Posted: Wed Feb 25, 2009 10:15 pm |
|
Joined: Thu Jan 10, 2008 8:49 pm Posts: 520 Location: New England
|
I don't know of any regulation that says you must maintain coordination. You must protect the cable at the ampacity its rated. If you meet that protection, but trip upstream protectors before downstream, you'll have obvious maintenance issues, but I don't know of any regulation you'd be violating.
|
|
Top |
|
 |
WDeanN
|
Post subject: Posted: Thu Feb 26, 2009 6:39 am |
|
Joined: Thu Jul 19, 2007 7:54 am Posts: 201 Location: St. Louis, MO
|
See NEC 240.12, 700.27, and 701.18
Basically the system must be selectively coordinated if it requires and orderly shutdown, if it is a legally required standby system, or an emergency power system.
|
|
Top |
|
 |
|