| Author: | Vica1ME [ Fri Feb 27, 2009 9:34 am ] |
| Post subject: | Incident Energy |
We express available incident energy in calories/square-cm. I'm a bit confused about the square-cm. I know how to convert watt-seconds to joules to calories of heat. How does the square-cm factor into the equation? |
|
| Author: | Zog [ Fri Feb 27, 2009 9:47 am ] |
| Post subject: | |
Vica1ME wrote: We express available incident energy in calories/square-cm. I'm a bit
confused about the square-cm. I know how to convert watt-seconds to joules to calories of heat. How does the square-cm factor into the equation? Think of Watt-seconds as energy released, when you talk about J or Cal/cm2 it is refering to that heat on a recieving surface, so to measure that you need to define the area of the recieving surface. |
|