bure961 wrote:
This timing issue could mean our ppe is not at the right level for protection against a fault? YES/NO?
It depends. This s not a black-and-white issue, and there are two directions to consider. First, failure to properly maintain equipment results in an increase in the likelihood of occurrence of an arc flash. In itself this is a bigger problem in my estimation because it's a relatively rare event in the first place and we'd like it to stay that way.
Case in point at a site that didn't do proper maintenance. Operators having trouble with a pump. Breaker (not overload) was tripping. After several attempts at resetting the molded case breaker in a 480 V MCC with no success, they called an electrician. Electrician arrives and does the exact same thing. Never mind the huge OSHA violation here. Eventually electrician gets out a meter and recognizes that motor is dead shorted to ground. Locks come out and motor gets replaced. Up to this point nobody had bothered to inspect the breaker as required by NEMA AB-4 and it was not inspected until after the incident. When electrician went to remove locks and close breaker in one last time to test equipment, breaker exploded and electrician was badly injured from arc flash. Oh, and the upstream breaker did work but at that time they didn't wear arc resistant PPE.
What happened here is a classic case of both improper mainteannce being done and no mainteannce being done at all up to this point. As I said, it increased the likelihood dramatically. The operator is just lucky that the electrician happened to be there when the breaker finally failed and not during all the attempts to close into a fault that were done up to that point.
Quote:
If the timing is off and the cb stays open longer than it should , are we not in trouble ?
Considering the increased hazard, fuses are basically electrochemical devices are are almost unaffected by age. They might trip sooner than expected but fuses that take longer than predicted to trip are very rare. All equipment in which the arc flash study got to the cutoff (usually 2 seconds) without tripping is also unaffected by equipment failures because there is no assumption that it will ever trip. Third, some equipment is just plain so low in terms of arc power that it never gets to the low level limit such as 1.2 cal/cm^2. So with respect to that equipment the incident energy study is still valid, even if the likelihood has dramatically increased and the breakers are all basically seized up scrap metal.
So I would have to answer the question with a qualified yes.
Quote:
We mention this to the company and the answer has always been about the PM cost of getting the work done. "we can t afford it now".
We are looking for ways to push the company into getting this done. It just doesn t seem right to do a study knowing your labels do not have the correct information on them. There is so much more I need to learn about this afs. Thanks again for listening.
Baby steps here. First, what about a simple IR scan? This is cheap and addresses one of the major causes of failures (loose connections) and the best part is that you don't even have to de-energize to do it, unless you made the mistake of "booby trapping" your medium voltage gear with door-trip switches so you can't open it while energized.
Second, did you actually generate a list of critical equipment yet that requires more than ""minimal" PM's? This would be:
1. Anything that production actually thinks is critical to life, health, etc. Think fire pumps and life support equipment.
2. Any breakers over 600 A frame sizes, especially molded case. Why? IEEE 493 documents that the failure rates on these are about 3 times higher than the smaller sizes.
3. Any breakers where failure would result in arc flash being higher than predicted. This usually means that for instance with an MCC, the "main" breaker needs to be PM'd but not the smaller ones, and 120/240 V lighting panels don't need an extensive PM either.
4. If you have electromechanical or solid state (not microprocessor) relays, at a minimum, pull the bucket out every 3 years and do the recommended time-current testing. Usually I only test 1 or 2 points on each function as a check and that's it. Reinsert the relay.
This means that all the little 15/20 A lighting panel breakers aren't touched unless they are on the critical list.
Mechanical issues (mostly lubrication) are the #1 cause of breaker issues. The #2 cause is problems with the trip electronics. If you can hit these two issues, you covered the vast majority of problems.
I would explain it like this with a standard list of questions:
1. Do you change your oil in your car/truck/SUV on a regular basis?
2. Do you check your air pressure and tire wear on a regular basis?
3. Do you check the pressure in your air conditioner on a regular basis?
Typically we all do #1 because we don't get very far without doing it. Fewer people do #2 but recognize the benefit (better gas mileage and fewer major expenses). Almost nobody does #3...we operate the air conditioner run-to-failure because it's a comfort/convenience item, even in the Southeast U.S. where I live.
With circuit breakers, exercising them and doing relubrication (changing the grease) is directly equivalent to #1. Doing the relay checking is equivalent to #2. And doing Doing that level of maintenance on a 15/20 A breaker in a lighting panel for the offices is equivalent to #3.
For some reason most people understand cars better than they do circuit breakers. But most people have dozens of circuit breakers in their houses and some don't even own a car. It's another one of those strange mysteries that we can't explain.