ekstra   ara
 Post subject: Modeling Single Phase Transformers
PostPosted: Mon Apr 27, 2015 11:16 am 

Joined: Tue Sep 29, 2009 8:44 pm
Posts: 6
As I recall, SKM used to have instructions on how to model a single phase transformer as a three phase transformer so when running a three phase short circuit study it would return the correct short circuit current without upgrading to the single phase/unbalanced module. There was a formula to "adjust" the parameters of a standard three phase transformer. I couldn't find it the help section of the current version and nobody at SKM tech support is old enough to remember this. Any help would be appreciated!

Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling Single Phase Transformers
PostPosted: Mon May 04, 2015 4:05 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 879
Location: Rutland, VT
I have a paper from EasyPower that explains how to model a single phase transformer on a 3 phase model (which EasyPower is). I would think it would be very similar for SKM.


You do not have the required permissions to view the files attached to this post.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Modeling Single Phase Transformers
PostPosted: Mon May 04, 2015 9:37 am 

Joined: Thu Sep 27, 2012 3:02 pm
Posts: 19
Location: Washington
This is from a Q&A posted on the PTW website.

In PTW, you can run a unbalanced short circuit study using the Unbalanced module.

Then enter the SLG fault current or using the 3P fault from UBSC results to the AF screen. PTW automatically unlinks the SC and link TCC. You can enter the adjusted fault current based on the UBSC results and Arc Flash program reads the trip time automatically. The results will be conservative, but having an answer is better than having no answer at all.

In the ArcFlash drop down menu check "Include Non-3-Phase Systems".

http://www.skm.com/Newsletter_April_2012.html


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883