ekstra   ara
 Post subject: Arc Flash Protection Boundary
PostPosted: Thu Feb 18, 2016 8:55 am 
Offline

Joined: Fri Nov 21, 2014 10:14 am
Posts: 15
Location: Fot McMurray, Alberta, Canada
Working on the Arc Flash Analysis i found that for a Low Voltage MCC Buss the AFB (10.56 inches) is less than the Limited Approach (42 inches) and Restricted Approach (12 inches). What could be wrong in my model?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Protection Boundary
PostPosted: Thu Feb 18, 2016 8:58 am 
Offline
Sparks Level
User avatar

Joined: Tue Nov 12, 2013 6:31 am
Posts: 237
Location: Port Huron, Michigan
jorgepaz wrote:
Working on the Arc Flash Analysis i found that for a Low Voltage MCC Buss the AFB (10.56 inches) is less than the Limited Approach (42 inches) and Restricted Approach (12 inches). What could be wrong in my model?


What's the incident energy? I'm betting it's well below 1.2 cal/cm2.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Protection Boundary
PostPosted: Thu Feb 18, 2016 9:23 am 
Offline

Joined: Fri Nov 21, 2014 10:14 am
Posts: 15
Location: Fot McMurray, Alberta, Canada
Yes it is 0.5 cal/cm2


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Protection Boundary
PostPosted: Thu Feb 18, 2016 10:51 am 
Offline
Sparks Level
User avatar

Joined: Tue Nov 12, 2013 6:31 am
Posts: 237
Location: Port Huron, Michigan
jorgepaz wrote:
Yes it is 0.5 cal/cm2


There's no reason that isn't possible. Can't say for sure without having your model.

The other boundaries you mention deal with shock hazard, and have nothing to do with arc flash hazard.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Protection Boundary
PostPosted: Thu Feb 18, 2016 11:54 am 
Offline

Joined: Fri Nov 21, 2014 10:14 am
Posts: 15
Location: Fot McMurray, Alberta, Canada
thx a lot.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Protection Boundary
PostPosted: Thu Feb 18, 2016 12:58 pm 
Offline
Sparks Level
User avatar

Joined: Wed Jun 10, 2009 5:00 pm
Posts: 204
Location: Toronto
jorgepaz wrote:
Working on the Arc Flash Analysis i found that for a Low Voltage MCC Buss the AFB (10.56 inches) is less than the Limited Approach (42 inches) and Restricted Approach (12 inches). What could be wrong in my model?


what is the arc duration? are you calculating the arc flash boundary based on actual incident energy to 2nd degree burn or based on 1.2 cal/cm^2?

_________________
Michael Furtak, C.E.T.
http://arcadvisor.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Protection Boundary
PostPosted: Thu Feb 18, 2016 1:43 pm 
Offline
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 1779
Location: North Carolina
jorgepaz wrote:
Working on the Arc Flash Analysis i found that for a Low Voltage MCC Buss the AFB (10.56 inches) is less than the Limited Approach (42 inches) and Restricted Approach (12 inches). What could be wrong in my model?


The original source for the shock protection boundaries is IEEE 516. NFPA 70E, NESC, and all subsections of OSHA regulations refer back to IEEE 516. I suggest reading this if you want to know the excruciating details. Below a certain voltage the limited approach boundary is fixed at 3'6" for everything except overhead lines (where it switches to 10'). Eventually it increases as the underlying flashover distance increases. The restricted approach boundary is fixed and somewhat arbitrary below 1 kV. Above that point it is calculated using the flashover distance plus a constant that accounts for inadvertent movement.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Protection Boundary
PostPosted: Mon Feb 22, 2016 9:32 am 
Offline
Sparks Level
User avatar

Joined: Sun Jan 04, 2009 5:00 pm
Posts: 248
Location: Louisville, KY
jorgepaz wrote:
Working on the Arc Flash Analysis i found that for a Low Voltage MCC Buss the AFB (10.56 inches) is less than the Limited Approach (42 inches) and Restricted Approach (12 inches). What could be wrong in my model?


This is not uncommon at all. The Limited Approach is a SHOCK boundary based on IEEE 516 with the idea that Limited is for UNQUALIFIED persons to remain safe since they do not know which parts are energized and could potentially TOUCH energized parts and be shocked. There is never correlation of Limited Approach and AFB.

Different hazards of the same device.

Hugh Hoagland
e-Hazard.com


Last edited by wbd on Tue Feb 23, 2016 5:32 am, edited 1 time in total.
removed personal contact info


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Protection Boundary
PostPosted: Mon Feb 22, 2016 10:23 am 
Offline

Joined: Fri Nov 21, 2014 10:14 am
Posts: 15
Location: Fot McMurray, Alberta, Canada
Thanks everyone for your response.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 9 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883