Post subject: Tables vs. Analysis Posted: Mon Mar 30, 2009 3:37 pm |
|
Joined: Tue Feb 17, 2009 11:04 am Posts: 37
|
130.3(A)(2) gives the parameters for the Arc Flash Protection Boundary when above 1000 volts. The FPN steers me to Annex D for estimating the boundary. Are there any default numbers for voltages above 1000 volts? If not, must this boundary be calculated? Thanks!
|
|
Top |
|
 |
Vincent B.
|
Post subject: Posted: Tue Mar 31, 2009 5:25 am |
|
Joined: Tue Feb 24, 2009 7:05 am Posts: 252
|
Basically, yes.
So then, you'll say "what's the point of using Table 130.3(C)(9) for tasks above 1 kV"? No idea.
|
|
Top |
|
 |
McFlash
|
Post subject: Posted: Fri Apr 03, 2009 9:27 am |
|
Sparks Level |
 |
Joined: Mon Nov 10, 2008 1:08 pm Posts: 60 Location: Cincinnat, OH
|
I think that you are talking about table 130.7(C)(9).That table has nothing to do with the Arc-Flash Protection Boundary. It deals with tasks once you are inside of that boundary. You need to calculate the boundary to properly apply table 130.7(C)(9).
I am in no way promoting the tables but if you are going to reference them and use them you must follow all application guidelines......meaning following all notes and FPN's as well as first establishing the proper boundary distance.
|
|
Top |
|
 |
|