Tables vs. Analysis
https://brainfiller.com/arcflashforum/viewtopic.php?f=2&t=389
Page 1 of 1

Author:  Vica1ME [ Mon Mar 30, 2009 3:37 pm ]
Post subject:  Tables vs. Analysis

130.3(A)(2) gives the parameters for the Arc Flash Protection Boundary when above 1000 volts. The FPN steers me to Annex D for estimating the boundary. Are there any default numbers for voltages above 1000 volts? If not, must this boundary be calculated? Thanks!

Author:  Vincent B. [ Tue Mar 31, 2009 5:25 am ]
Post subject: 

Basically, yes.

So then, you'll say "what's the point of using Table 130.3(C)(9) for tasks above 1 kV"? No idea.

Author:  McFlash [ Fri Apr 03, 2009 9:27 am ]
Post subject: 

I think that you are talking about table 130.7(C)(9).That table has nothing to do with the Arc-Flash Protection Boundary. It deals with tasks once you are inside of that boundary. You need to calculate the boundary to properly apply table 130.7(C)(9).

I am in no way promoting the tables but if you are going to reference them and use them you must follow all application guidelines......meaning following all notes and FPN's as well as first establishing the proper boundary distance.