| Author: | Ex twidget [ Fri Apr 17, 2009 12:10 pm ] |
| Post subject: | Interacting With Equipment |
Interacting With Equipment is discussed on various threads. Is there a general consensus on what this means, other than what's in the 130.7(C)(9) tables? There are a couple specific cases that come to mind, these both apply to facilities with calculated IE levels and AFBs:
Both of these aren't uncommon evolutions. Are they considered live work? Interaction with equipment in a manner which may cause an arc flash? I appreciate input from the arc flash community. |
|
| Author: | Zog [ Fri Apr 17, 2009 12:17 pm ] |
| Post subject: | |
70E defines live work as work within the LAB, so IMO both are live work. (#1 may depend on the configuration of the equipment) |
|
| Author: | Ex twidget [ Fri Apr 17, 2009 12:28 pm ] |
| Post subject: | |
Zog, I see the definitions for "exposed" and for "working on" in 70E. "Working on" is explicitly defined as direct contact. "exposed" is a little vague. Using the limited approach boundary to define live work puts us at 3'-6" for LV systems, which would include just opening doors or IR scanning in the hot work category. It seems like those things can be done without even breaking the plane. |
|
| Author: | Zog [ Fri Apr 17, 2009 1:00 pm ] |
| Post subject: | |
Hmm, the 2004 version made that clear but you are right, they changed the definition to "clarify" it, which now has me confused. Now I am going to have to re-think this one. Geez, just when you think you have it all figured out |
|
| Author: | mayanees [ Wed Apr 22, 2009 4:49 am ] |
| Post subject: | |
[quote="Ex twidget"]Interacting With Equipment is discussed on various threads. Is there a general consensus on what this means, other than what's in the 130.7(C)(9) tables? QUOTE] Et: I think the answer to the interaction question is in section 90.2 Scope (A) Covered, which reads: This standard addresses electrical safety requirements for employee workplaces that are necessary for the practical safeguarding of employees during activities such as the installation, operation, maintenance, and demolition of electric...... I think those italicized words represent "interaction". .. which means that an operator of the equipment is at risk wihile within the Arc-Flash Boundary (AFB), and therefore needs exposed-bus PPE. And, if you're working on a BPS that's been isolated, but is within the AFB of another panel, I'd think you'd need to meet the other panels PPE requirement while interacting; installing fuses. John M |
|