 Post subject: Rooms with exposed energized equipment
PostPosted: Fri Apr 24, 2009 6:25 am 
Offline

Joined: Wed Nov 12, 2008 7:02 am
Posts: 2
One of the projects we are working on there is a room with exposed motor starters on the walls. We have decided to label the door to the room. These starters run about 3 feet apart there are two substations feeding these starters. I have 3 questions:

1. Could an arc flash on one starter encompass and initiate an arc on another starter?

2. If so, would the incident energy be additive?

3. How would you account for this in the calculation?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed May 06, 2009 7:44 pm 
Offline
Sparks Level

Joined: Thu Oct 18, 2007 7:10 pm
Posts: 250
Location: NW USA
It is unlikely that an arc flash event on a LOW VOLTAGE system would cause another arc flash event on an adjacent system 3 feet away, unless molten metal/ plasma was projected in that direction. A medium voltage arc might jump to adjacent systems 3 feet away, but it is unlikely there would be different systems unguarded so close together. I would expect that Arc Flash energy could be added, but the question is suspicious.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jun 02, 2009 2:55 pm 
Offline

Joined: Tue Jun 02, 2009 1:40 pm
Posts: 19
Need more informaiton, low voltage, medium voltage, kva of source all would be good starts.

It is possible to have the plasma cloud from a meltdown move to adjacent equipment but the bigger danger is it moving up the supply line conductors and that would be bad.

What happened to the requirement that exposed equipment be guarded? Does the room have a fence seperating the starters from the rest of the room. Would the arc flash boundry extend beyond the fence.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Jun 04, 2009 9:38 pm 
Offline

Joined: Sat May 30, 2009 6:21 pm
Posts: 19
it's probably an old plant i have seen this once
no low voltage was enclosed
you had to be carefull is was running a 3000hp 600Vdc motor and large spark were seen when the motor was changing direction every 5 second or so :eek:


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883