Would a Harmonic Correction Unit impact the incident energy during an arc flash in an MCC line-up? :?: :|


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Harmonic Correction Unit?
PostPosted: Wed Jul 20, 2016 3:33 pm 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
jdelgado wrote:
Would a Harmonic Correction Unit impact the incident energy during an arc flash in an MCC line-up? :?: :|


It depends on what type it is. There are lots of ways to do "harmonic correction".

If it is some kind of filter, whether it consists of just series inductors, or just parallel capacitors, or a combination of both (LC filters), the result is that you are adding impedance to the system even though it is frequency-sensitive. This decreases the available fault current and hence the arcing current. Although this sounds like it will reduce incident energy if the overcurrent protective device is working on an inverse time curve then the net result is that it increases rather than decreases incident energy because it will take longer for the overcurrent protection to trip.

If it's a UPS or equivalently a "line conditioner" where it is essentially a cycloconverter and if there are no non-semiconductor paths through the device then the semiconductor acts as a very fast fuse or will be protected by very fast fusing and thus incident energy will be low due to current limitations of the semiconductors.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Harmonic Correction Unit?
PostPosted: Wed Jul 20, 2016 3:35 pm 

Joined: Sun Jun 26, 2016 9:00 pm
Posts: 7
Thanks! :)


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883