jdelgado wrote:
Do I find the normal operating current by taking the MCA and dividing it by 1.25? seems right....

The term normal operating current is a little confusing. MCA is 125% of the largest load, plus 100% of the rest. The largest load could be either a motor, as in the case of a condensing unit, or could be resistance heat, in the case of an air handler. Starting currents, inrush, etc. have nothing to do with MCA