 Post subject: 100A panel with 200A "gutter mounted" main. WTF??
PostPosted: Thu Oct 27, 2016 8:28 am 
Sparks Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 285
Location: Indiana
Came across this today while surveying. The original drawing shows this panel with a 100A branch mounted main. Well, someone needed that breaker for another panel and removed it and installed this instead.

Not in the photo: 4/0 feeder spliced inside an adjacent panel with #2. #2 goes through wireway to this 200A "gutter mounted" MCB which had been removed from the adjacent panel. Adjacent panel was re-fed from a different source. Sheesh!

Oh, and the 4/0 feeder (and the #2 splice, and the 200A gutter main and the 100A panel) are protected with 200A fuses.

Attachment:
BA cover on.jpg


Attachment:
BA cover off.jpg


Attachment:
BA gutter main.jpg


You do not have the required permissions to view the files attached to this post.

_________________
SKM jockey for hire


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 100A panel with 200A "gutter mounted" main. WTF??
PostPosted: Sun Oct 30, 2016 4:30 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1710
Location: Scottsdale, Arizona
Gives new meaning to "field installed" Just curious, what happened next i.e. pointing this out to the owner and their response?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 100A panel with 200A "gutter mounted" main. WTF??
PostPosted: Mon Oct 31, 2016 4:06 am 
Sparks Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 285
Location: Indiana
Jim Phillips (brainfiller) wrote:
Gives new meaning to "field installed" Just curious, what happened next i.e. pointing this out to the owner and their response?


I work in facilities at a university so I guess you could say I am the Owner. I got with our on staff electricians and they took out that "main", landed the feeder on the buss and changed the fuses out back at the distribution board to 100A. Everyone claims ignorance as to when, who and how that got installed. I'm still not wild about the feeder passing through another panel cabinet but at least it is electrically safe now. We'll re-do the feeder when we can schedule a shutdown for that panel.

_________________
SKM jockey for hire


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 100A panel with 200A "gutter mounted" main. WTF??
PostPosted: Mon Oct 31, 2016 11:04 am 
Sparks Level

Joined: Mon Jun 07, 2010 9:40 am
Posts: 119
Let us not ignore the use of white wire for phase conductors either..... :)


What type of breaker was that?


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883