Will there be 8 steps to establish an Electrically Safe Work Condition? If so, what are the 2 new steps? Thanks in advance for your response.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 2018 70E
PostPosted: Tue Aug 01, 2017 2:27 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1702
Location: Scottsdale, Arizona
Yes, verification of an electrically safe work condition was relocated from 120.1 to 120.5 and two new steps were added:

(4) Release stored electrical energy
(5) Release or block stored mechanical energy

They are inserted at position 4 and 5 in the list of steps for a total of 8.

2018 NFPA 70E Changes Article


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 2018 70E
PostPosted: Wed Aug 02, 2017 11:55 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2173
Location: North Carolina
Jim Phillips (brainfiller) wrote:
Yes, verification of an electrically safe work condition was relocated from 120.1 to 120.5 and two new steps were added:

(4) Release stored electrical energy
(5) Release or block stored mechanical energy

They are inserted at position 4 and 5 in the list of steps for a total of 8.

2018 NFPA 70E Changes Article


Interesting. No matter how many times I look at it, "grounding" is one of those things that nobody can seem to agree on. Prior to this version draining capacitive charge (discharge stored electrical energy) was all but absent from any standard or regulation. It generally gets tied up with two other steps...applying grounding and testing for absence of voltage.

There are definitely 3 different issues to be addessed...discharging stored charges, shorting things out to avoid actual existing voltages that cannot be eliminated (e.g. two overhead lines on the same pole structure with different circuits), and testing to make sure that there is no residual voltage. There are different orders to these steps in both 70E and NESC but get it wrong and the result can be physically very hazardous.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883