It is currently Sat Nov 07, 2026 6:50 pm



Post new topic Reply to topic
Author Message
 Post subject: ARCPRO vs IEEE results of AFIE
PostPosted: Fri Jan 19, 2018 1:28 pm 
Sparks Level

Joined: Sat Apr 04, 2009 9:50 pm
Posts: 122
Location: San Antonio, TX
I would like to know where can I find a comparative analysis of the results of AFIE from ARCPRO and IEEE 1584 for both, three-phase and single phase circuits.

I know that IEEE 1584 excludes single-phase circuits but IEEE 1584.1 allows the use of IEEE 1584 equations for single-phase circuits assuming that they are three phase and considering that will result in conservative results.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: ARCPRO vs IEEE results of AFIE
PostPosted: Tue Jan 23, 2018 3:13 pm 
Sparks Level
User avatar

Joined: Sun Jan 04, 2009 5:00 pm
Posts: 288
Location: Louisville, KY
The easiest way is to purchase and compare.

They will be much lower on Medium Voltage systems.

Kinectrics teaches a class on this as do we. Jim may even have this type of comparison in his excellent classes.

I see these as two tools in the toolbox.

Use ArcPro 3.0 as it is a great update.

Hugh Hoagland


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883