| 277V Arc Flash Hazard? https://brainfiller.com/arcflashforum/viewtopic.php?f=2&t=463 |
Page 1 of 1 |
| Author: | ZeroSeq [ Mon Jun 08, 2009 11:47 am ] |
| Post subject: | 277V Arc Flash Hazard? |
I know that most AF software only covers three phase systems, but is there any field experience with arc flashes on single phase 277V lighting circuits? Would OSHA consider a 277V arc flash a '[color="Red"]recognized hazard[/color]' under Section 5(a)(1)? OSH Act of 1970 http://www.osha.gov/pls/oshaweb/owasrch.search_form?p_doc_type=OSHACT&p_toc_level=0&p_keyvalue=&p_status=CURRENT SEC. 5. Duties (a) Each employer -- (1) shall furnish to each of his employees employment and a place of employment which are free from [color="Red"]recognized hazards[/color] that are causing or are likely to cause death or serious physical harm to his employees; |
| Author: | haze10 [ Mon Jun 08, 2009 7:11 pm ] |
| Post subject: | |
I would say that it would need to be considered because it is 240 and greater, even if fed from less than 125KVA xfrm. Most of us are using the 3 phase equations until a single phase model is developed. |
| Author: | jghrist [ Tue Jun 09, 2009 7:56 am ] |
| Post subject: | |
I concur with haze10. Assume that the fault can develop into a 3Ø 480 volt fault. Do this as a conservative assumption even if the other phases are not present because there is no industry accepted way to calculate the energy otherwise. |
| Author: | Noah [ Wed Jun 10, 2009 5:50 am ] |
| Post subject: | |
Duke's heat flux calculator does the job for single phase arc fault in air but requires arc current input. Take a loot at this: http://www.arcadvisor.com/pdf/DukeHeatFluxCalculatorGuide.pdf |
| Author: | ZeroSeq [ Fri Jul 10, 2009 9:58 am ] |
| Post subject: | |
Here's an example of 277v single phase causing an explosion. (I'm assuming was a 277v fixture.) Does this mean we should do AF calcs and put AF warning labels on every 277v lighting fixture? http://www.ktla.com/news/landing/ktla-hospital-evacuated,0,1235173.story KTLA Explosion Prompts Evacuation of SoCal Hospital KTLA News July 10, 2009 GLENDORA -- Authorities say part of Foothill Presbyterian Hospital in Glendora was evacuated early this morning after a flourescent light fixture suddenly exploded. The incident occurred around 12:45 a.m. in the emergency room of the facility, which is located on South Grand Avenue. When firefighters arrived, two hospital employees and a civilian complained of eye irritation, but all declined treatment, according to a Los Angeles County Fire Department dispatch supervisor. Firefighters evacuated the emergency room while hospital maintenance crews searched for the source of the explosion. The emergency room was expected to reopen sometime before 3 a.m., the dispatch supervisor said. The explosion was traced to a lighting ballast, which maintains the electrical current in fluorescent fixtures. |