MTE wrote:
Agree, but note that the generator leads are actually insulated. No copper is exposed, just the leads themselves are within site and are not inside a TB or conduit box.
The word exposed doesn't mean you can see copper and this is a very common misconception. Shock protection is not required where energized conductors are insulated, guarded (visible but behind some kind of barrier that prevents inadvertent contact), or not exposed. Exposed is sort of a catch all that captures things such as conductors that are not accessible such as overhead power lines, or behind some kind of panel where blind reaching is either not being done or not possible. Inside modern MCC buckets when you open the door even though there are clearly power and control cables plainly visible if they are properly terminated, nothing is exposed. All of it is either guarded, insulated, or not exposed by covers. Exposed also has to be evaluated by distance. For instance if I'm working outside the restricted approach boundary (which also includes additional distance to account for inadvertent movement...hence 480 VAC has a 12" boundary with a little under 1" of arcing, and 11" of buffer space for inadvertent movement).
Most generators have a lot of little control wires running around them and a few power conductors where the ends are terminated with little to no gaps. MCC buckets are the same way, and with either one with the doors open everything is guarded, insulated, or not exposed, at least when it comes from the factory. What the end users do to a piece of equipment is an entirely different story. I don't mind...more business for me to repair the stuff that blew up.