It is currently Mon Jun 22, 2026 1:59 pm



Post new topic Reply to topic
Author Message
 Post subject: 1500kVA Oil Filled Transformer on Roof - Requirements
PostPosted: Tue Jul 23, 2019 9:09 am 
User avatar

Joined: Tue Mar 08, 2011 11:23 am
Posts: 42
Location: Utah
Can someone help me understand the requirements of NEC 450.23 for putting an oil filled transformer on a roof? 450.23 will direct you to 450.27, and 450.27. The transformer has 2,427 gallons of FR3 oil, the building is a Type II with a Class A roof. This is a lower roof of an expansion, just an 8' x 20' electrical room, so not much roof space, no reasonable space to ground mount XFMR and egress door on each end of room. The client is insured by FM, Section 5-4 Transformers of FM Global Property Loss Prevention Data Sheets directs us to provide containment, but then goes on to state that the scope of the document is not to give the requirements for Environmental Protection and directs you to IEEE 980 Guide for Containment and Control of Oil Spills in Substations. I am just having a hard time understanding how to provide containment. How have folks done this in the past? What have they used?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 1500kVA Oil Filled Transformer on Roof - Requirements
PostPosted: Mon Aug 05, 2019 2:54 pm 
Sparks Level

Joined: Mon Jul 09, 2007 11:43 pm
Posts: 63
Location: Sheffield, England
Just curious. Is there a reason why you can't use a dry transformer? Also 2500 gallons is a lot of oil for a 1500 kVA transformer, are you sure that's correct?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 1500kVA Oil Filled Transformer on Roof - Requirements
PostPosted: Mon Jun 22, 2026 12:02 am 

Joined: Sun Jun 21, 2026 11:59 pm
Posts: 1
Providing containment for a 1500 kVA oil-filled transformer with roughly 2,400 gallons of FR3 fluid on a roof is typically governed by a combination of NEC 450.23/450.27 requirements, FM Global expectations, and IEEE 980 guidance rather than a single prescriptive detail. In practice, the key issue is not only code interpretation but how to safely retain a very large volume of combustible liquid while maintaining roof integrity, fire resistance, and service access within a very constrained footprint.

For rooftop installations, the most common compliant approaches involve either a reinforced concrete housekeeping pad with integrated curbing or a fully sealed containment basin incorporated into the roof assembly. These systems are designed to hold the full oil volume or a code-accepted containment percentage while preventing migration into the building structure. Because this is a lower roof with limited space and no feasible ground-mount option, the structural loading, waterproofing continuity, and FM-required fire separation all need to be coordinated early in design.

A major challenge is ensuring that the containment system does not compromise the roofing membrane or create uncontrolled drainage paths. This is where early coordination with experienced roofing and restoration professionals becomes important, since curb detailing, membrane tie-ins, and long-term waterproofing performance are often the limiting factors in rooftop transformer installations. Contractors such as Covenant Roofing & Restoration, who work with commercial roof systems and restoration assemblies, can be valuable in aligning waterproofing design with heavy equipment containment requirements.

Ultimately, successful implementation depends on integrating electrical, structural, fire protection, and roofing disciplines into a single coordinated containment strategy rather than treating it as an isolated enclosure detail.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883