danocap1982 wrote:
I think I have more information. The comment from the customer I now understand to mean that they can not operate the breaker locally (while standing in front of the switchgear). This is different than my original understanding that they said they could not operate it at all.
That said, I still cannot find any NFPA 70E upper limit of 70 - 75 Cal/cm^2 as they state in NFPA 70E 2015 or 2018...?
A bit of additional info to go along with the comments from Mayanees. NFPA 70E does not specifically call out 40 cal/cm^2 for operating a circuit breaker. This likely was referencing the informational note about de-energize above 40 cal/cm^2 which was deleted in the 2018 edition. There isn't a reference to 70-75 cal/cm^2 in NFPA 70E