bfietkau wrote:
Why is PPE determination based on Volts and not Current?
It is not based on voltage at all, but rather the totoal amp-cycles of the fault and the distance from the arc to the worker.
bfietkau wrote:
All of the safety guys that I work with say that since our guys were not working with over 600V they did not require PPE as per the standard. Now after reviewing the 2009 NFPA 70E we know different.
Typically you will find higher (larger) arc flash hazards on LV equipment than you will on anything >600V.
bfietkau wrote:
But I still do not understand the Volts ideology when determining PPE.
Not sure what you mean or where you get that from, please explain.
bfietkau wrote:
Thanks I look forward to coming back on a regular basis.
We are glad to have you, may I suggest you read some old posts, get a feel for what an arc flash is, etc...